What size equipment grounding conductor is necessary for a propane tank on a residence with a 200amp electrical service? Is a bare grounding wire suitable ran underground? If so, how deep should the bare grounding wire be buried? This grounding wire would not have any energized wires with it. Only the grounding wire. Would it be a #6 equipment grounding conductor for the propane tank according to table 250.122?
2017 NEC 250.104(B) Other Metal Piping.
If installed in or attached to a building or structure, a metal piping system(s),
including gas piping, that is
likely to become energized shall be bonded to any of the following:
- (1) Equipment grounding conductor for the circuit that is likely to energize the piping system
- (2) Service equipment enclosure
- (3) Grounded conductor at the service
- (4) Grounding electrode conductor, if of sufficient size
- (5) One or more grounding electrodes used, if the grounding electrode conductor or bonding jumper to the grounding electrode is of sufficient size
The bonding conductor(s) or jumper(s) shall be sized in accordance with
Table 250.122, and equipment grounding conductors shall be sized in accordance with
Table 250.122 using the rating of the circuit that is likely to energize the piping system(s). The points of attachment of the bonding jumper(s) shall be accessible.
Key words for bonding requirement "likely to become energized". Is your propane tank likely to become energized? What is circuit rating that is likely to energize the pipe to the tank?
But like don said:
The NEC does not require the tank to be bonded.