Grounding A Separately Derived System

Status
Not open for further replies.

blues

Member
Location
Nevada
I have a transformer feeding a 480volt switchgear with a 3200 main circuit breaker. We are supplying this switchgear with 9-3 conductor #500kcmil tray rated cable. My question is the multi-conductor cable is provided with 1-#2awg ground conductor. I am still required to provide the proper size ground conductor per table 250.66.

Thanks Dan
 

Smart $

Esteemed Member
Location
Ohio
I have a transformer feeding a 480volt switchgear with a 3200 main circuit breaker. We are supplying this switchgear with 9-3 conductor #500kcmil tray rated cable. My question is the multi-conductor cable is provided with 1-#2awg ground conductor. I am still required to provide the proper size ground conductor per table 250.66.

Thanks Dan
Yes (assuming you mean supply-side bonding jumper). Each cable would have to have a 1/0 copper grounding conductor to be compliant.
 

bob

Senior Member
Location
Alabama
Smart, If all of the cables are in the same tray, does he need more than one 1/0 ground for the 9 cables?
 

Smart $

Esteemed Member
Location
Ohio
Smart, If all of the cables are in the same tray, does he need more than one 1/0 ground for the 9 cables?
1/0 per cable is compliant with 250.102(C)(2).

The only alternative is to use a single SSBJ. 250.102(C)(2) refers that to 250.102(C)(1) sizing, which over 1100 kcmil copper is 12.5%.

500kcmil ? 9 = 4500kcmil .... ? 12.5% = 562.5kcmil

I don't know of any allowance to use metal tray as an SSBJ. 392.60 only says it can be used as an EGC.
 

bob

Senior Member
Location
Alabama
Thanks for your detail post. I was trying to point out the use of 1 conductor rather that the 9.
 

topgone

Senior Member
Thanks for your detail post. I was trying to point out the use of 1 conductor rather that the 9.

That would be nice but didn't the OP say those 9 x 3C cables have a #2awg each?

9 x 66,360 Cmils = 597,240 Cmils, which is almost 6 times bigger than a single 1/0 awg (105,600 Cmils).
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
That would be nice but didn't the OP say those 9 x 3C cables have a #2awg each?

9 x 66,360 Cmils = 597,240 Cmils, which is almost 6 times bigger than a single 1/0 awg (105,600 Cmils).

A #2awg in each cable is too small. As Smart$ pointed out, EACH cable would have to have a 1/0awg. Or a single SSBJ would have to be 600mcm.
 