Answered hereWhere lies the danger from hooking up this generator to a panel without breaking the neutral path at the service?
No. The three-pole transfer switch, by breaking the neutral, actually creates two completely separate systems. The EGC is never in parallel with the neutral.Won't that still happen via the EGC's being connected to both sources?
If the transfer switch is on the line side of the main, do you think it makes any difference?is installed between the electric meter and the main panel in an existing home,
A transfer switch "installed between the electric meter and the main panel in an existing home" must become the 'main'.Originally posted by russ:
I don't think the transfer switch would be considered the main. I don't think they all have external arms to shut them off.
IMO a transfer switch installed between an existing electric meter and existing service disconnect becomes the new service disconnect.transfer switches marked, ??SUITABLE FOR USE AS SERVICE EQUIPMENT?? are provided with accessible means to independently disconnect both the normal and alternate sources.
Isn't that what I suggested in the last sentence of the previous posting? The only problem is that the price of such a switch can be a lot more than the cost of the MLO kit and the 3R enclosure for the main breaker. If you have a source for a cost effective service rated transfer switch that contains the Over Current Protective Devices (OCPD) in the same enclosure I would be most grateful if you would share it.Originally posted by iwire:
Tom your recommending a lot of labor when simply buying a service rated transfer switch with integral OCP would solve any issues.
Tom if this thread was talking about an Auto Transfer switch I would agree. I believe this thread is talking about a manual transfer switch.Originally posted by hornetd:
The only problem is that the price of such a switch can be a lot more than the cost of the MLO kit and the 3R enclosure for the main breaker. If you have a source for a cost effective service rated transfer switch that contains the Over Current Protective Devices (OCPD) in the same enclosure I would be most grateful if you would share it.--
That is not a true statement...many currently available portable generators do not have any of the conductors bonded to anything.All portable generators come with a bonded neutral.
Glancing at the posts above (this thread has had quite a bump list, looking at the dates! ), I don't understand what you mean by "same situation as above". A few different setups were described.leggo said:If a home has the neutral and EGC bonded together at the transfer switch, in the same situation as above, and only has a 3 wire SE cable coming out of transfer switch to the main breaker panel in the house, where the grounds and neutrals are not separated, would this burn up the generator and cause it to stop working?
That is interesting, thank you, Don. I didn't know that.Don said:That is not a true statement...many currently available portable generators do not have any of the conductors bonded to anything.