A step down 75KVA 3 phase wye transformer 490/277 to 208/120 recently went bad, it was located inside a building servicing a motor aparently it did not have a ground connection, my question is
would that be a possible cause why the transformer went bad?
 

Smart $

Esteemed Member
Location
Ohio
A step down 75KVA 3 phase wye transformer 490/277 to 208/120 recently went bad, it was located inside a building servicing a motor aparently it did not have a ground connection, my question is
would that be a possible cause why the transformer went bad?
IMO, not being grounded would not cause failure.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I agree. Lack of a ground would be way down on my list of possibilities.

Can you tell us how it was connected (Input 480v ?, was the 480/277 neutral connected to anything ? )
 

conmgt

Senior Member
Location
2 Phase Philly
What do you mean by bad? Internal short such as a breakdown in insulation or meltdown from overloading? Failure of the motor overloads? Low voltage on the primary side?
 

Sparky Adam

Master Electrician
Location
Dallas, TX
Occupation
Operations Manager / Master Electrician
Probably dust build up on the plates... And if the humidity was high you could have a bridge for the current to flow.
 