I will take 312.5 (C) for 100$ Alex.
Normally for a GEC I would not, but sheesh, going through the grate.
I will take 312.5 (C) for 100$ Alex.
312.1 Scope. This article covers the installation and con-struction specifications of cabinets, cutout boxes, and meter socket enclosures.
Also see 450.10 "shall not be installed on or over any vented portion of the enclosure"
450.10 Grounding.
(A) Dry-Type Transformer . Ellclosures. Where separate equipment grounding conductors and supply-side bonding jumpers are instaJIed, a tenhinal· bar for alL grounding. and bonding conductor connections shall be secured inside the transformer enclosure. The terminal bar sha.ll be bonded to the enclosure in accordance· with 250.12 and shall not be installed on or over any· vented portion of the. enclosure.
I do not see anything there preventing bringing the GEC through the vents.