Grounding a transformer.

Status
Not open for further replies.

Danny89

Member
Location
Indian Land
I have a few transformers at my plant that are grounded to building steel the building steel at some point is grounded to the water pipe feeding our building.

Does this seem to code?

There is no water pipes by the transformer.
I'm guessing this would be ok. As long as at some point the building steel attached to the water pipe at some point...?

Sent from my Moto Z (2) using Tapatalk
 

tom baker

First Chief Moderator
Staff member
Your quesiton is too incomplete to answer.
What is the voltage and configuration (480 delta x 120/208 Wye)?
Transformers are required to have a connection from the XO terminal via a grounding electrode conductor to a grounding electrode, which can be building steel.
There is also required to be system bondinng jumper from the XO terminal to the metal case of the transformer.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I have a few transformers at my plant that are grounded to building steel the building steel at some point is grounded to the water pipe feeding our building.

Does this seem to code?

Probably yes, providing there is a system bonding jumper too as Tom mentioned.
 

david

Senior Member
Location
Pennsylvania
I have a few transformers at my plant that are grounded to building steel the building steel at some point is grounded to the water pipe feeding our building.

Does this seem to code?

There is no water pipes by the transformer.
I'm guessing this would be ok. As long as at some point the building steel attached to the water pipe at some point...?

Sent from my Moto Z (2) using Tapatalk

your code reference would be 250.104 (D)
 

david

Senior Member
Location
Pennsylvania
are there metal water pipes in the area served by the secondary derived system

is there a bond between the grounding electrode and the metal water pipe system in the area served by the secondary derived system?

you stated there are no water pipes by the transformer, that is not the same thing as the area served by the transformer secondary
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
your code reference would be 250.104 (D)

I think I would be more likely to be guided by 250.30.
If the installers knew enough to bond to building steel I would say odds are the install is compliant.
 

david

Senior Member
Location
Pennsylvania
I think I would be more likely to be guided by 250.30.
If the installers knew enough to bond to building steel I would say odds are the install is compliant.

250.30 (A) (8) bonding
250.104 (D)

it has bee my experience most installers do not know the metal water system needs to be looked at for bonding

once the grounding electrode conductor is installed to building steel they are done
 
Last edited:

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
250.30 (A) (8) bonding
250.104 (D)

it has bee my experience most installers do not know the metal water system needs to be looked at for bonding

once the grounding electrode conductor is installed to building steel they are done

My apology, I had misread the OP thinking he was questioning the bonding of the transformer in general.
250.104 and it's exceptions are indeed very relevant.
 