I am the inspector on an airport taxiway extension and the contractor is using a AEMC "clamp-on" ground resistance meter and getting extra high readings. (in the 77 ohm range) and I am getting readings in the range of 6.5 to 16 ohms with a three wire Extech 382252 meter. these reading are on a 5/8 X 8' ground rode installed at each Taxiway light. I have been told by a registered PE in Electrical Engineering that the clamp on meter will give false reading without a return path (like two ground rods at several ft. apart) connected to the light. FAA and NEC both require 25 ohms or less. Any input on this subject would be appreciated