So I've seen some threads that may touch on this but I'm still confused.
I have a machine with a 480/120 3KVA xformer. Though the machine will be fixed during use we'd like to be able to pull it out for maintenance so we want to avoid additional connections. The machine builder says the low side of the xformer needs to be grounded to building steel or a grounding electrode per 250.30. My reading of 250 makes me think they are correct but I think we have quite a few machines that aren't grounded this way so one of us is wrong. I thought we may qualify for Exception 2, which speaks to the supply of the SDS being located inside of equipment rated as Suitable for Use as Service Equipment but don't see a lot of information on what qualifies equipment as SUSE.
Thanks for reading.
I have a machine with a 480/120 3KVA xformer. Though the machine will be fixed during use we'd like to be able to pull it out for maintenance so we want to avoid additional connections. The machine builder says the low side of the xformer needs to be grounded to building steel or a grounding electrode per 250.30. My reading of 250 makes me think they are correct but I think we have quite a few machines that aren't grounded this way so one of us is wrong. I thought we may qualify for Exception 2, which speaks to the supply of the SDS being located inside of equipment rated as Suitable for Use as Service Equipment but don't see a lot of information on what qualifies equipment as SUSE.