I have a 200 amp underground, ungrounded 3 wire single phase residential service. Installing a home standby generator. Service goes as: Consists of 4 panels outside
200A meter base- 200A non fused disconnect- 200A service rated ATS panel- 200A main breaker outdoor 16 circuit panel with sub panels,hvac etc… breakers
I have 3 wire from meter base to non fused disconnect > 3 wire run from non fused disc. To ATS > 4 wire run from ATS to 8/16 main breaker panel. 4 wire run from main breaker panel to sub panels and all grounded and grounding separated in main breaker panel and after I was going off 250.186A exception, 250.186B exception and 250.30 inspector says I have to separate my N-G in the ATS because the non fused is my first means of disconnect. Doing so will cause the generator itself to become a sds.
200A meter base- 200A non fused disconnect- 200A service rated ATS panel- 200A main breaker outdoor 16 circuit panel with sub panels,hvac etc… breakers
I have 3 wire from meter base to non fused disconnect > 3 wire run from non fused disc. To ATS > 4 wire run from ATS to 8/16 main breaker panel. 4 wire run from main breaker panel to sub panels and all grounded and grounding separated in main breaker panel and after I was going off 250.186A exception, 250.186B exception and 250.30 inspector says I have to separate my N-G in the ATS because the non fused is my first means of disconnect. Doing so will cause the generator itself to become a sds.