grounding and bonding question, meter feeds disconnect to ats to disconnect to gen set. Ats to main ac panel. Do u remove the bond to neutral in second disconnect that feeds gen set?
Thanks
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

As with any other service, everything downstream of the main disconnect/OCPD is wired without neutral/ground bonding.

Of course, a generator is a source, not a load, but, yes, the generator feeder and disconnect are usually also un-bonded.
 

TonyTW

Member
Location
Canada
Occupation
Industrial Electrician
Welcome to the forum.

As with any other service, everything downstream of the main disconnect/OCPD is wired without neutral/ground bonding.

Of course, a generator is a source, not a load, but, yes, the generator feeder and disconnect are usually also un-bonded.
K that’s what I did but noticed a different contractor left the neutral bond screw in when they did same set up in different building. I only left screw in at main disconnect.
 