ctaylo360860
Senior Member
- Location
- colorado
- Occupation
- ME
Here is the plant that I'm working on, the systems, equipment, and work I'm inquiring about is all existing. I work in house for the company and am trying to get the GEC system right. I have not been able to find a bonding jumper to the structural metal you see in the picture below.... Im sure it is needed according to 250.104 (C) structural metal, but wanted to confirm.. see pictures 6 & 7
![wetplant3.jpg wetplant3.jpg](https://forums.mikeholt.com/data/attachments/27/27103-8a117ad2520c16cf67347c003e510be1.jpg)
This picture below is the 400a service disconnect, 75kva transformer, and the 208/120v panel. The 400-amp service is fed with (2) parallel runs of 3/0 copper service conductors, and (2) paralleled #2copper for the grounded conductor. the only GEC i have found is #2 that goes to a single ground rod outside see picture #4, and another #2 that goes to a water pipe. The plumbers got a hold of the water pipe since the main line broke outside. They ended up cutting it off outside and then inside and shoved a piece of 3/4 pex through the 1-1/4 copper line. since they have done this it is no longer part of my grounding electrode system... see pictures 6 and 7
![IMG_1526.JPG IMG_1526.JPG](https://forums.mikeholt.com/data/attachments/27/27110-608b2409a9686d7b71713ef8b8408bc6.jpg)
75 kva transformer fed from 100 a cb with (4) # 2 copper conductors. 3 phases and a EGC
![wetplant1.jpg wetplant1.jpg](https://forums.mikeholt.com/data/attachments/27/27101-bae298a4b66d1875cff4f7fa2428dcff.jpg)
Only ground rod found for the Grounding electrode sytem.
![wetplant2.jpg wetplant2.jpg](https://forums.mikeholt.com/data/attachments/27/27102-d4439852b672d06d67d5bf2ccffbf915.jpg)
I'm wondering if this structural metal needs to be bonded to the grounding electrode system? I would use 250.102(C)(1) to size the bonding jumper from the grounded conductor at the service to the structural metal... the other way i thought about handling this was setting a copper bus bar connector running 3/0 copper from the service disconnect to the bus bar connector. Then i believe i would need to run a 1/0 copper conductor from the busbar connector to the steel. I thought about doing it this way so that i could land the GEC from the 208/120 panel to the busbar connector as well. it should be sized according to 250.66 and because the 208/120 panel is fed with 3/0 copper i would need to run a #4cu from where my sbj is to the busbar connector
![wetplant4.jpg wetplant4.jpg](https://forums.mikeholt.com/data/attachments/27/27104-fa15c9ad1e95644cb82644a9ee1810dc.jpg)
any reason #2 would be needed to the water pipe? i thought #4 was the largest size needed.
![wetplant5.jpg wetplant5.jpg](https://forums.mikeholt.com/data/attachments/27/27105-589ace4154a3bdaf02d30a06930b605e.jpg)
Plumbers in the wild...
![wetplant 6.jpg wetplant 6.jpg](https://forums.mikeholt.com/data/attachments/27/27106-52c71b141029f4e257c578bdcbb4512b.jpg)
this is the 75 kva transformer fed from a 100a circuit breaker. the ran (3) 3/0 copper conductors for phases. (1) #2 copper for the grounded conductor, and (1) #8 as the EGC. the had the separately derived system bonded at transformer and the 208/120 panel... i unbonded the grounded and grounding conductors at the 75kva transformer. looks the the egc going to the 208/120 panel needs to be atlease a #6 or larger... i say this because the egc is going to a panel that has a 200amp ocpd. looks like they sized it based on the primary 100a ocpd...
![wetplant9.jpg wetplant9.jpg](https://forums.mikeholt.com/data/attachments/27/27109-5411851012da4ff368f593b1e4e5d786.jpg)
208/120v panel fed from 75kva transformer. panel is bonded and the egc is undersized. because i have my grounding and grounded conductors bonded in this panel using the system bonding jumper strap i need to run my GEC from the neutral bar where strap is located to either the service disconnect grounded conductor bar. or if i go the other route and use a copper bus bar connector. the size of my gec will be based on 250.66 the 208/120 panel is fed with 3/0 copper and my gec should be a size #4 or largerl
![wetplant8.jpg wetplant8.jpg](https://forums.mikeholt.com/data/attachments/27/27108-e923536c2d16e666e86dfe9be6b18798.jpg)
#8 egc from 75kva transfromer to 208/120 panel
![wetplant7.jpg wetplant7.jpg](https://forums.mikeholt.com/data/attachments/27/27107-42613b3bee2cfc6c7037631318ad4d75.jpg)
Thanks in advance for any and all help its always appreciated!
![wetplant3.jpg wetplant3.jpg](https://forums.mikeholt.com/data/attachments/27/27103-8a117ad2520c16cf67347c003e510be1.jpg)
This picture below is the 400a service disconnect, 75kva transformer, and the 208/120v panel. The 400-amp service is fed with (2) parallel runs of 3/0 copper service conductors, and (2) paralleled #2copper for the grounded conductor. the only GEC i have found is #2 that goes to a single ground rod outside see picture #4, and another #2 that goes to a water pipe. The plumbers got a hold of the water pipe since the main line broke outside. They ended up cutting it off outside and then inside and shoved a piece of 3/4 pex through the 1-1/4 copper line. since they have done this it is no longer part of my grounding electrode system... see pictures 6 and 7
![IMG_1526.JPG IMG_1526.JPG](https://forums.mikeholt.com/data/attachments/27/27110-608b2409a9686d7b71713ef8b8408bc6.jpg)
75 kva transformer fed from 100 a cb with (4) # 2 copper conductors. 3 phases and a EGC
![wetplant1.jpg wetplant1.jpg](https://forums.mikeholt.com/data/attachments/27/27101-bae298a4b66d1875cff4f7fa2428dcff.jpg)
Only ground rod found for the Grounding electrode sytem.
![wetplant2.jpg wetplant2.jpg](https://forums.mikeholt.com/data/attachments/27/27102-d4439852b672d06d67d5bf2ccffbf915.jpg)
I'm wondering if this structural metal needs to be bonded to the grounding electrode system? I would use 250.102(C)(1) to size the bonding jumper from the grounded conductor at the service to the structural metal... the other way i thought about handling this was setting a copper bus bar connector running 3/0 copper from the service disconnect to the bus bar connector. Then i believe i would need to run a 1/0 copper conductor from the busbar connector to the steel. I thought about doing it this way so that i could land the GEC from the 208/120 panel to the busbar connector as well. it should be sized according to 250.66 and because the 208/120 panel is fed with 3/0 copper i would need to run a #4cu from where my sbj is to the busbar connector
![wetplant4.jpg wetplant4.jpg](https://forums.mikeholt.com/data/attachments/27/27104-fa15c9ad1e95644cb82644a9ee1810dc.jpg)
any reason #2 would be needed to the water pipe? i thought #4 was the largest size needed.
![wetplant5.jpg wetplant5.jpg](https://forums.mikeholt.com/data/attachments/27/27105-589ace4154a3bdaf02d30a06930b605e.jpg)
Plumbers in the wild...
![wetplant 6.jpg wetplant 6.jpg](https://forums.mikeholt.com/data/attachments/27/27106-52c71b141029f4e257c578bdcbb4512b.jpg)
this is the 75 kva transformer fed from a 100a circuit breaker. the ran (3) 3/0 copper conductors for phases. (1) #2 copper for the grounded conductor, and (1) #8 as the EGC. the had the separately derived system bonded at transformer and the 208/120 panel... i unbonded the grounded and grounding conductors at the 75kva transformer. looks the the egc going to the 208/120 panel needs to be atlease a #6 or larger... i say this because the egc is going to a panel that has a 200amp ocpd. looks like they sized it based on the primary 100a ocpd...
![wetplant9.jpg wetplant9.jpg](https://forums.mikeholt.com/data/attachments/27/27109-5411851012da4ff368f593b1e4e5d786.jpg)
208/120v panel fed from 75kva transformer. panel is bonded and the egc is undersized. because i have my grounding and grounded conductors bonded in this panel using the system bonding jumper strap i need to run my GEC from the neutral bar where strap is located to either the service disconnect grounded conductor bar. or if i go the other route and use a copper bus bar connector. the size of my gec will be based on 250.66 the 208/120 panel is fed with 3/0 copper and my gec should be a size #4 or largerl
![wetplant8.jpg wetplant8.jpg](https://forums.mikeholt.com/data/attachments/27/27108-e923536c2d16e666e86dfe9be6b18798.jpg)
#8 egc from 75kva transfromer to 208/120 panel
![wetplant7.jpg wetplant7.jpg](https://forums.mikeholt.com/data/attachments/27/27107-42613b3bee2cfc6c7037631318ad4d75.jpg)
Thanks in advance for any and all help its always appreciated!