I have a project (in bid) that has four (4) buildings and a single 800A service. The main distribution panel is located in the exterior of building D.
Building A has two (2) panels from MDB each 200A. This building is CMU and steel support with a 1"C water pipe (copper).
Building B has one (1) panel from MDB also 200A. This building is CMU and steel support with a 1-1/4"C water pipe (copper).
Building C has one (1) panel from MDB at 60A. Building C is CMU and steel support.
Building D has (1) panel from MDB with 100A. This building is CMU with steel decking.
When grounding separate buildings from a single service, 250.32 (A) states, "...shall have a grounding electrode or grounding electrode system installed in accordance with Part III of Article 250." Part III of Article 250 states, "All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system."
Please correct me if I'm wrong but, this means I would have my grounding electrode (from the same conduit as my current carrying conductors) and this electrode would be connected to each building's; metal underground water pipe, metal in-ground support structure, and concrete-encased electrode.
Building A has two (2) panels from MDB each 200A. This building is CMU and steel support with a 1"C water pipe (copper).
Building B has one (1) panel from MDB also 200A. This building is CMU and steel support with a 1-1/4"C water pipe (copper).
Building C has one (1) panel from MDB at 60A. Building C is CMU and steel support.
Building D has (1) panel from MDB with 100A. This building is CMU with steel decking.
When grounding separate buildings from a single service, 250.32 (A) states, "...shall have a grounding electrode or grounding electrode system installed in accordance with Part III of Article 250." Part III of Article 250 states, "All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system."
Please correct me if I'm wrong but, this means I would have my grounding electrode (from the same conduit as my current carrying conductors) and this electrode would be connected to each building's; metal underground water pipe, metal in-ground support structure, and concrete-encased electrode.