We have a PM in place here at our plant where we semi-annually go around to each motor with a microhmeter and check the resistance between the motor case and the surrounding steel structure. The purpose of this test is to prove that the motors or equipment are adequately grounded. We refer to these tests and "ground continuity tests" Almost all of the time, the readings that we get are less than an ohm.
The problem that I have with this test, is that all we are really doing is measuring the resistance of the bonded steel between the motor case and whatever part of the stell building we are taking our reading. This proves that there is continuity between the motor case and building structure. This does not prove however there is a low resistance path back to the source for clearing faults. This is obviously the purpose of the EGC. Also what is to say that the building structure has a low resistance path back to the source, or any path for that matter. Aside from that the NEC prohibits any part of a building or structure to be used as an EGC.
We perform these checks in order to provide to MSHA should they ask during an inspection which sometimes they do.
My question is, by performing these checks the only thing that I can see we are doing, it proving that the motor is bonded to the surrounded building to eliminate any touch potentials if the motor was faulted.
We are not proving at all that the motor has an low resistance path back to the ground bus in the form of an EGC. This would be a hard test to prove I think. I have heard in some cases where plants pull an extra conductor with their feeds and use this extra conductor for performing continuity checks on the EGC.
What do you guys think of this PM we are performing and its validity?
The problem that I have with this test, is that all we are really doing is measuring the resistance of the bonded steel between the motor case and whatever part of the stell building we are taking our reading. This proves that there is continuity between the motor case and building structure. This does not prove however there is a low resistance path back to the source for clearing faults. This is obviously the purpose of the EGC. Also what is to say that the building structure has a low resistance path back to the source, or any path for that matter. Aside from that the NEC prohibits any part of a building or structure to be used as an EGC.
We perform these checks in order to provide to MSHA should they ask during an inspection which sometimes they do.
My question is, by performing these checks the only thing that I can see we are doing, it proving that the motor is bonded to the surrounded building to eliminate any touch potentials if the motor was faulted.
We are not proving at all that the motor has an low resistance path back to the ground bus in the form of an EGC. This would be a hard test to prove I think. I have heard in some cases where plants pull an extra conductor with their feeds and use this extra conductor for performing continuity checks on the EGC.
What do you guys think of this PM we are performing and its validity?