Grounding and bonding question
wireman1
According to article 250.66 the size of the grounding electrode conductor
does not have to be bigger than 3/0 copper or 250 aluminum. Example:
a 2,000 amp service in which you run 6 - 3 inch rigid conduit pipes each
containing 3 thwn 500 mcm copper conductors which you paralell for a
2,000 amp service. The size of the grounding conductor would be a 3/0
copper conductor, yet the size of the wire for the bonding bushings on the
rigid pipes would have to be 12 1/2 percent of the total circular mill area
of the 6 - 500 mcm cables to bond all the pipes together.
Could you take a size 1/0 wire from each rigid pipe to the grounding bar
located in the switch gear and accomplish the same thing?
Would this be acceptable by the code?