Re: grounding and bonding with subpanels
Miscommunication is the devil, Bobby!
Alpinemike wrote:
The ground wire is landed on the dist. panel neutral, not the meter neutral.
That's legal. The meter isn't the service disconnecting means, the panel is. (250.24)
There is a distribution panel with a breaker that feeds a main panel in the house via 2" pvc, with no bonding wire in the pipe.
This is where it's getting fuzzy Mike. I see:
1. 200 Amp Service on a pole.
2. 200 Panel on a pole (maybe the same thing).
3. 2" PVC from this pole-panel to interior of the house's main panel.
Violation of 225.31-ish, the disconnecting means for a remote structure must be outside or inside nearest the entrance of conductors. There is no EGC, which if there are no other metallic paths, is legal.
What size conductors are in this pipe? What size breaker?
4.
Main Panel in House. There is a #6 ground wire to the water pipe. Depending on the size of conductors, this could be legal or not. Mike never specified that this panel was fed with conductors big enough for 200A. I'm thinking there could be other circuits from the outside pole panel, and the house is less than 200A.
The neutal bar in the inside main panel has a #6 ground taken to the water pipe. When I take the wire off the water pipe , the resistance between neutral and ground goes to megohm.
You have an EGC somewhere in the house touching the water pipe. That's legal. The reason things are behaving that way is because the water pipe was landed on the neutral bar of the panel.
When everything was hooked up, juice in your meter was leaving the red probe, travelling through the EGC's until it reached water heater, or whatever was making contact with the water pipe. Then it was travelling back along the GEC to the neutral bar of the panel where it was landed. So you had continuity between neutral and ground until you removed the electrode conductor, breaking the circuit.
Install an appropriate bonding jumper between the neutral and grounding bar of this main panel. Reinstall the GEC, and supplement it with a ground rod.
5.
The main house panel feeds a 100 amp sub panel via 4-3 romex . We installed that panel and put a separate ground bar in it.
Is this
new or old romex? Is there a EGC with it? The water pipe is not in this panel, is it?
From this point in your post, you went a little chaotic, so I am really confused.
Can you write out a "one-line diagram", filling in the gaps? When you hop back and forth, it makes it impossible for us to make sense enough to help you.