Grounding and Bonding

Status
Not open for further replies.

tompoff43

Member
Location
Cincinnati
Occupation
Electrical designer
Does anyone have experience with ground and bonding for a steel roller coaster? Looking foe NEC requirements if any.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
I would think supports and track would be considered building steel. See 250.104(C) among other sections. I do not believe a roller coaster is different than a steel frame building as far as the NEC is concerned.

Note that the NEC is not a lightning protection standard.
 

retirede

Senior Member
Location
Illinois
Nothing in the NEC that I can think of. There are a handful of ASTM standards covering amusement park rides. I’d expect that electrical requirements would be covered in them somewhere.
 