Grounding Autotransformer Overcurrent Protection
beanland
Vancouver, WA
2011 NEC 450.5(B)(2)(b) requires overcurrent protection for a grounding transformer at 125% of rating but specifically states that delay of tripping for proper function is allowed. This means that a thermal or overload element is required but that neither a short-time nor instantaneous (magnetic) element is required. I am looking for a molded case 480V 3-phase circuit breaker that has a thermal element but no magnetic element or, if electronic, has neither short-time nor instantaneous elements. I am totally unable to find anything. Square D even has a FAQ that states they do not offer any thermal-only circuit breakers.
In the utility industry, working with high-voltage breakers, we often have time delayed only elements, but the equipment is $1000's.
I need a 100A 480V 3-pole thermal-only breaker.
Does any one know of a manufacturer?
No. All of the CBs that I have seen, in that frame size have an inherent instantaneous trip. In fact, all of the molded case CBs of any frame size (that I have seen) have an inherent instantaneous trip.
As I recall, there are hi instantaneous trip CBs listed in the catalogs. Perhaps one of those is high enough to be out of the way
iceworm
No such animal exists
I've seen power (SWGR listed to UL-1066) circuit breakers that have an instantaneous element that can be disabled, but we are feeding 30 cycle rated equipment for those applications.