When there is no neutral, it is common to ground a phase. With the exception of not fusing it (3-phase breakers are okay), you treat it just like any 3-phase Delta system, but you bond and color it like any grounded conductor.bgtires said:Why do you intentually take a phase on a Delta to Delta system and put right to ground?
bgtires said:Why do you intentually take a phase on a Delta to Delta system and put right to ground?
A 3-phase breaker is okay because the internal common-trip and tie handle on the breaker open all poles simultaneously, whereas a fused disconnect can open only one pole, so a non-fused link (dummy fuse) must be used in the grounded pole.bgtires said:We are using fuses. The transformer has a breaker in it, but from there we go to a fuse disconnect.
sandsnow said:Using equip that "looks" like single phase but is rated for 240V 3 phase grounded B Phase ...