Re: Grounding Bar Kit
Creative backcountry wiring is amazing. but,
Without wasting too much time on unrelated particulars, this house is in a city, it's mine, it's not a rental unit, it's not for sale. The inspector is a city inspector with 40 years of experience. I think he is accustomed to bare bones installations. (When he first came to the house, before the installation began , he saw ground rods in the corner and said I would only need one. I said I would be installing a minimum of two. He said, they only do that in the suburbs where they have too much time on their hands.)
I also heard someone from another state say that they have had inspectors tell them to remove equipment grounding bars from their panel installations, so I believe this is an issue that hasn't been resolved.
I will have to study this , if I determine that it is absolutely definitely code, nationally and in this city, then I will have to figure out how to present it to him because I really want these equp.grnd bar kits installed.
This house is structurally a duplex.
The drop from the pole connects to copper at the weatherhead, runs to a milbank 2-hub meter pan. Both sides bonded w/#4. The meter base has the capability of 200 continuous amps/side. At this time, in a concession to inspector, and because it works for me at this time, I am running only 100 amps /side.
First side, copper leaves the meter pan in metal conduit, attaches to a sq d main breaker load center. Neutral green screw bond attached. When viewed by the inspector, #4 was attached to the installed equipment ground bar and ran from there, at least 50 ft. to the metal waterline entry point. A second #4 attached to the same equip grnd bar ran outside and attached successively to copper ground rods in sandy soil. A gfci receptacle installed adjacent to the panel attached to a 15 amp breaker and the ground wire attached to the second equipmet grounding bar.
The second meter side , copper runs through metal conduit and attaches to a square d 100 amp breaker disconnect. 2 - #4 solids attach to sq d installed ground lugs in this disco and attach to the electrodes running from the first panel. Right now they are attached with split bolt connectors, but I have the copper irreversible connectors and a non-hydraulic version of the necessary crimping tool and plan to change the connections.
Wire sizes: 2/0 from weatherhead, #3 to the disco, #3 to the panel, #4 solid ground for all.
Conduit size: 2" from weatherhead, 1" from meter.
Panel installed main breaker down (side to side on/off). (This first came up in a phone call to the inspections dept. and they made it the basis for an allround joke, they thought my call was a 'set up.' They said they never heard of such a thing. )
Inspector green tagged the installation for energizing. But asked for g.bar removal and asked that the three grounds that he could see be attached to the neutral busbar. He also asked for irreversible connections where the grounds met.
I think that's everything.