johnpbrewer
Member
- Location
- Eden Prairie, MN
Our product is battery powered, 7.2VDC, and contained in aplastic enclosure. We have options forsensor inputs and can provide 5V power to sensors. We are not sure of the grounding requirementsin both ordinary locations and hazardous locations.
Looking at the NEC in Article 250.160, our system will notrequire a ground since it is 2 wire DCand under 60V. However, we do haveprovision for a ground connection in our enclosure and would run a bondingjumper to that through a cable gland entry. We have some transient protection circuitry referenced to ground. I assume this will be OK. 250.102 (A) and 250.118 (1) both allow wireconductors.
For Class 1 Div 2 installations, however, the NEC states in501.30 that regardless of the voltage of the electrical system, wiring andequipment in Class I Division 1 and 2 locations shall be grounded as specifiedin Article 250 and in accordance with requirements of 501.30 (A) and (B).
Is a wire bonding jumper allowed per 501.30 (A)? Is conduit or flexible metal conduit required? 501.10 (B), Wiring Methods for Class I,division 2, does not list bondingjumpers. However, Exhibit 501.13 shows abonding jumper tied to flexible metal conduit to ensure effective connections, sincethe conduit is not considered a robust EGC in Class I Division 2. Since we have a plastic enclosure,only a bonding jumper through a cable gland will be used. Is thisacceptable?
Looking at the NEC in Article 250.160, our system will notrequire a ground since it is 2 wire DCand under 60V. However, we do haveprovision for a ground connection in our enclosure and would run a bondingjumper to that through a cable gland entry. We have some transient protection circuitry referenced to ground. I assume this will be OK. 250.102 (A) and 250.118 (1) both allow wireconductors.
For Class 1 Div 2 installations, however, the NEC states in501.30 that regardless of the voltage of the electrical system, wiring andequipment in Class I Division 1 and 2 locations shall be grounded as specifiedin Article 250 and in accordance with requirements of 501.30 (A) and (B).
Is a wire bonding jumper allowed per 501.30 (A)? Is conduit or flexible metal conduit required? 501.10 (B), Wiring Methods for Class I,division 2, does not list bondingjumpers. However, Exhibit 501.13 shows abonding jumper tied to flexible metal conduit to ensure effective connections, sincethe conduit is not considered a robust EGC in Class I Division 2. Since we have a plastic enclosure,only a bonding jumper through a cable gland will be used. Is thisacceptable?