I have a 480 volt 3 wire (no neutral) feed between two structures run in PVC. It feeds an MCC (Service) that contains a bucket for a transformer that provides a 120/208 secondary service. The engineer claims that the NEC does not require that an equipment ground be run with this feed between structures. I maintain that with neither a neutral nor a ground between the structures, there is no low impedance path to trip the breaker in a ground fault condition. Is this correct? If so, where does the NEC support this? Additional Information: I don't know whether there is continuous underground water piping between structures. A shielded fire alarm cable was pulled between the structures and the only way to get rid of nuisance alarms was to bond the shield at both structures. I believe the problem was caused by different potentials between the two structures. However, the equipment manufacturer says to insulate the shield everywhere except at the main FACP. If we cannot install a ground in the PVC with the feeder, is it acceptable to install a bond conductor in the fire alarm conduit so that we can isolate the shield per the manufacturer's recommendation?