Grounding/Bonding bar in IT closet/room, wire size requirement

Status
Not open for further replies.

victor.cherkashi

Senior Member
Location
NYC, NY
Hi forum members,
I can't find if there any requirement in NEC or any other code for wires size to/from Grounding/Bonding bar installed in IT closet/room. Since each receptacle for equipment in that closet/room is provided with EGC, the Grounding/Bonding bar on wall is serving for other purposes.
See the picture below, is there any minimum wire size requirement in code for wire size #1, #2, #3, #4
 

Attachments

  • bounding bar 3.JPG
    bounding bar 3.JPG
    133.5 KB · Views: 6
Last edited:
This is what I thought, the wire sizes (connected to IT bonding bar) are not NEC's concern.
If you you google "BICSI and TIA 607-B & ISO/IEC 30129" you find table with recommended cross section depended on wire length. #6 wire is minimum recommended for 13ft or less.
 