grounding / bonding cable tray

Status
Not open for further replies.

DW98

Member
? been asked before, but not completely sure I understand. Where cable tray is not intended to be an equipment grounding conductor, but is mechanically continuously and attached to building steel structure which is bonded, is it considered bonded. is there still a requirement for an equipment grounding conductor?
 
If "the cable tray is not intended to be an equipment grounding conductor", then by definition it cannot be counted as an EGC.
If you intend it to be an EGC and assure that all the conditions are met for it to be an EGC, then you can count it as an EGC and may not be required to also run a wire EGC. In some cases the NEC requires a wire EGC in addition to any raceway EGC.

Sent from my XT1585 using Tapatalk
 
If "the cable tray is not intended to be an equipment grounding conductor", then by definition it cannot be counted as an EGC.
If you intend it to be an EGC and assure that all the conditions are met for it to be an EGC, then you can count it as an EGC and may not be required to also run a wire EGC. In some cases the NEC requires a wire EGC in addition to any raceway EGC.

Sent from my XT1585 using Tapatalk

My read on this is that he does not want or need to use it as an EGC.

He just wants to know if it still needs to be bonded. I don't know the answer to that, I suspect yes.
 
My read on this is that he does not want or need to use it as an EGC.

He just wants to know if it still needs to be bonded. I don't know the answer to that, I suspect yes.
" is there still a requirement for an equipment grounding conductor?"

I don't see how you can justify your interpretation based on that sentence.
:)

Sent from my XT1585 using Tapatalk
 
My read on this is that he does not want or need to use it as an EGC.

He just wants to know if it still needs to be bonded. I don't know the answer to that, I suspect yes.
Your suspicion is correct. It's a fundamental 250.4 requirement. You may have to dig a bit through the Subsections to determine which case applies, but basically, if it could become energized, it must be bonded. If I understand the OP description correctly, it sounds like it is.
 
thanks for the replies. I've been rereading NEC 2008 392.7 (A) which references 250.96(A). I think instead of "is it considered bonded" in original post, I should have asked "it is considered grounded". I'm getting hung up on difference between grounding and bonding. If cable tray components are mechanically connected and the cable tray is then mechanically connected.to building steel which is connected to grounding electrode system, it is considered grounded?
 
Your suspicion is correct. It's a fundamental 250.4 requirement. You may have to dig a bit through the Subsections to determine which case applies, but basically, if it could become energized, it must be bonded. If I understand the OP description correctly, it sounds like it is.
I agree... but I've run across a couple AHJ's that insist on a bonding jumper. When challenged, they offer the following highlighted passage as "guidance" for their interpretation...

250.136 Equipment Considered Grounded. Under the
conditions specified in 250.136(A) and (B), the normally
non–current-carrying metal parts of the equipment shall be
considered grounded.

(A) Equipment Secured to Grounded Metal Supports.
Electrical equipment secured to and in electrical contact
with a metal rack or structure provided for its support and
connected to an equipment grounding conductor by one of
the means indicated in 250.134. The structural metal frame
of a building shall not be used as the required equipment
grounding conductor for ac equipment.

(B) Metal Car Frames. Metal car frames supported by
metal hoisting cables attached to or running over metal
sheaves or drums of elevator machines that are connected
to an equipment grounding conductor by one of the methods
indicated in 250.134.

As you know, grounding "likely to become energized" non-current-carrying metal parts is to be done with the equipment grounding conductor of the circuit of which would do the energizing.

Yes... it is highly debatable. Is only bonding required or must it be equipment grounded. The requirements are ambiguous at best.
 
thanks for the replies. I've been rereading NEC 2008 392.7 (A) which references 250.96(A). I think instead of "is it considered bonded" in original post, I should have asked "it is considered grounded". I'm getting hung up on difference between grounding and bonding. If cable tray components are mechanically connected and the cable tray is then mechanically connected.to building steel which is connected to grounding electrode system, it is considered grounded?

I would say that it is bonded to the grounding system.

Best, simplest, description I have heard was from Mike Holt when he once said--GROUNDING is done at one point--the point of service and goes to earth--BONDING is hooking everything else together and then to the grounding system at the point of service to provide a path for fault current
 