In the North Eastern States when you install a service for a residental dwelling with city water, you install a ground
rod with the coccect sized ground wire to the meter pan. Next you install a properly sized grounding conductor to
the water meter (street side) and shunt it to the house side and terminate at the neutral bus in the panelboard.
Therefore, you have a complete (low resistance) reference palne to ground.
Now here in Florida the EC is required to install a Ufer/Concrete Encased Electrode and terminate in the meter
pan, Ok. Next the copper piping (generally) at the hot water heater a grounding conductor in installed and a
connection is made to the copper piping. The other end is connected to the panel, Ok.
Now what happens if all the plumbing system in all non-mettalic (except for the hose bibs and facuets)? Now you
are solely relaying on the Ufer/Concrete Encased Electrode as the sole point for the grounding plane. As I metioned
in an earlier post, the footer is installed with a plastic vapor barrier between the footer and earth. Thus reducing the
surface area to acheive a low resistence to ground, as required by the NEC.
To my understanding (and I am not an engineeer) the grounding resistance is made up of the type of
electrode used, contact resistance between the electrode and the resistance of the soil. I have also read the
IEEE 4.2.3 and appears to me that the more surface area the better chances to acheive a low resistance to ground
would be. So now that a plastic vapor barrier in installed between the footer and the Ufer/CEE, how would this affect the grounding system? To me this would reduce the total surface area that is in contact with the earth. Now that the plumbers are using non-metallic piping systems how (if any) deos this affect theoveral grounding system?
At this point I think that an independant test should be preformed on the CEE to determine what the resistance is,
and that it is in compliance with the NEC.
Would love to hear everbody's comments.
...We accept the norm as a standard and run with it without question, but when we alter from the norm we still
don't question it ..... we just accept it.
"Can Do'
rod with the coccect sized ground wire to the meter pan. Next you install a properly sized grounding conductor to
the water meter (street side) and shunt it to the house side and terminate at the neutral bus in the panelboard.
Therefore, you have a complete (low resistance) reference palne to ground.
Now here in Florida the EC is required to install a Ufer/Concrete Encased Electrode and terminate in the meter
pan, Ok. Next the copper piping (generally) at the hot water heater a grounding conductor in installed and a
connection is made to the copper piping. The other end is connected to the panel, Ok.
Now what happens if all the plumbing system in all non-mettalic (except for the hose bibs and facuets)? Now you
are solely relaying on the Ufer/Concrete Encased Electrode as the sole point for the grounding plane. As I metioned
in an earlier post, the footer is installed with a plastic vapor barrier between the footer and earth. Thus reducing the
surface area to acheive a low resistence to ground, as required by the NEC.
To my understanding (and I am not an engineeer) the grounding resistance is made up of the type of
electrode used, contact resistance between the electrode and the resistance of the soil. I have also read the
IEEE 4.2.3 and appears to me that the more surface area the better chances to acheive a low resistance to ground
would be. So now that a plastic vapor barrier in installed between the footer and the Ufer/CEE, how would this affect the grounding system? To me this would reduce the total surface area that is in contact with the earth. Now that the plumbers are using non-metallic piping systems how (if any) deos this affect theoveral grounding system?
At this point I think that an independant test should be preformed on the CEE to determine what the resistance is,
and that it is in compliance with the NEC.
Would love to hear everbody's comments.
...We accept the norm as a standard and run with it without question, but when we alter from the norm we still
don't question it ..... we just accept it.