Engineering drwing calls for:
Building grounding electrode with #3
Cold water pipe #3/0 (pex from the street to building convert to metal riser)
Building steel #3 (building does have any steel.)
Footer steel #3 (only 20' rebar, all other steel is coated.)
And ground rod #3.
Service to building is 1200A with two sets of 600Kcmil
NEC refers to 1/0 for 600Kcmil 250.66 for GEC, except that rod or concere encased electrode (footer steel) not be required to be larger than #6 for rod & #4 for Ufer.
What should be the code requirements for this senario?
Thanks,
Building grounding electrode with #3
Cold water pipe #3/0 (pex from the street to building convert to metal riser)
Building steel #3 (building does have any steel.)
Footer steel #3 (only 20' rebar, all other steel is coated.)
And ground rod #3.
Service to building is 1200A with two sets of 600Kcmil
NEC refers to 1/0 for 600Kcmil 250.66 for GEC, except that rod or concere encased electrode (footer steel) not be required to be larger than #6 for rod & #4 for Ufer.
What should be the code requirements for this senario?