commonslob
Member
hello hello
Been working on some condos and have just started tying in some services. I'm finding myself slightly confused with the ground system. The main service on three of the buildings is 400 amp 500 mcm conductors, the buildings have a water main, sprinkler main and #4 AWG connected to the footing. I was given a roll of #4 to run to the water and sprinkler mains and use as the main bonding jumpers. After looking in the book to refresh my memory I'm thinking this is no good. Now I'm not the foreman of this job but would like to know if my thinking is right so I can point it out if things need corrcting. There's a breakneck pace and a failed inspection could mess up the schedule. This is what I've come up with, please correct me if i'm wrong and point me in the right direction
My main bonding jumper needs to be 1/0
I need to run a 1/0 from the main panel to the water main
the bond to the sprinkler main should be 1/0? (thinking 250.104 A(1))
I can connect the #4 from the footing to the ground bar on the main panel (in one building the #4 will not reach, connecting it to the 1/0 as it passes by on the way to the water pipe is acceptable, right?)
Also the main panel also feeds panels in a second building. I need to bond the water and sprinkler pipes in that building too right? Would running a bond wire sized to the equipment ground of the largest panel in the second building to the ground bar of that panel be the correct way to do this?
Thanks much for your help, sorry if these are basic questions, but I'm used to simple house services where the main bonding jumper is just a screw and there are no sprinklers
Been working on some condos and have just started tying in some services. I'm finding myself slightly confused with the ground system. The main service on three of the buildings is 400 amp 500 mcm conductors, the buildings have a water main, sprinkler main and #4 AWG connected to the footing. I was given a roll of #4 to run to the water and sprinkler mains and use as the main bonding jumpers. After looking in the book to refresh my memory I'm thinking this is no good. Now I'm not the foreman of this job but would like to know if my thinking is right so I can point it out if things need corrcting. There's a breakneck pace and a failed inspection could mess up the schedule. This is what I've come up with, please correct me if i'm wrong and point me in the right direction
My main bonding jumper needs to be 1/0
I need to run a 1/0 from the main panel to the water main
the bond to the sprinkler main should be 1/0? (thinking 250.104 A(1))
I can connect the #4 from the footing to the ground bar on the main panel (in one building the #4 will not reach, connecting it to the 1/0 as it passes by on the way to the water pipe is acceptable, right?)
Also the main panel also feeds panels in a second building. I need to bond the water and sprinkler pipes in that building too right? Would running a bond wire sized to the equipment ground of the largest panel in the second building to the ground bar of that panel be the correct way to do this?
Thanks much for your help, sorry if these are basic questions, but I'm used to simple house services where the main bonding jumper is just a screw and there are no sprinklers