Please help a homeowner.
Main House - 400 AMP Service Panel. Murray. Villa Park, California. Orange County.
Detached Garage - approx 50 feet from panel. Inside a 3/4 PVC pipe 2 #6 THHN Black Wires, 1 #6 THHN White Wire, and 1 #10 THHN Green wire were run. Connected at Main Panel to double 60 AMP breaker, Neutral, and Ground.
In the Detached Garage a Murray Sub Panel.
Disagreement between the Electrician and the Inspector.
Electrician says install a grounding bus in the box and connect the #10 green to it, connect the White to the neutral Bus. Do not bond them, keep them isolated, and DO NOT install a grounding rod. Logic is if house loses white and ground, then #10 Green becomes a heating coil.
Inspector says - all I know is code - Install a Grounding rod, connect it to the Neutral Bus along with the green wire. No separate ground bus, all green/white go on the same bus.
Help please?
Main House - 400 AMP Service Panel. Murray. Villa Park, California. Orange County.
Detached Garage - approx 50 feet from panel. Inside a 3/4 PVC pipe 2 #6 THHN Black Wires, 1 #6 THHN White Wire, and 1 #10 THHN Green wire were run. Connected at Main Panel to double 60 AMP breaker, Neutral, and Ground.
In the Detached Garage a Murray Sub Panel.
Disagreement between the Electrician and the Inspector.
Electrician says install a grounding bus in the box and connect the #10 green to it, connect the White to the neutral Bus. Do not bond them, keep them isolated, and DO NOT install a grounding rod. Logic is if house loses white and ground, then #10 Green becomes a heating coil.
Inspector says - all I know is code - Install a Grounding rod, connect it to the Neutral Bus along with the green wire. No separate ground bus, all green/white go on the same bus.
Help please?