Hi all,
I am reading the NEC code 2020
250.2B:
(B) Alternating-Current Systems 50V to 1,000V.
The following systems must be grounded (connected to a grounding electrode) where the neutral conductor is used as a circuit conductor:
(1) Single-phase systems
(2) Three-phase, wye-connected systems.
(3)Three-phase, high-leg delta-connected systems.
here it says it must be grounded however in 250.21, it seems like I can still technically not ground my system...
(B) Ground Detectors. Ungrounded alternating-current systems from 50V to 1,000V or less are not required to be grounded if:
(1) The ungrounded systems operating between 120V and 1,000V as permitted in 250.21 (A) have ground detectors installed on the system.
(2) The ground detection sensing equipment is connected as close as practicable to where the system receives its supply.
here are my questions:
1. Can I unground my single-phase system but ground all the metal cases?
2. what is the pros and cons if I unground this system?
3. if I measure the L1/L2 to the ground, what voltage I would expect?
I am reading the NEC code 2020
250.2B:
(B) Alternating-Current Systems 50V to 1,000V.
The following systems must be grounded (connected to a grounding electrode) where the neutral conductor is used as a circuit conductor:
(1) Single-phase systems
(2) Three-phase, wye-connected systems.
(3)Three-phase, high-leg delta-connected systems.
here it says it must be grounded however in 250.21, it seems like I can still technically not ground my system...
(B) Ground Detectors. Ungrounded alternating-current systems from 50V to 1,000V or less are not required to be grounded if:
(1) The ungrounded systems operating between 120V and 1,000V as permitted in 250.21 (A) have ground detectors installed on the system.
(2) The ground detection sensing equipment is connected as close as practicable to where the system receives its supply.
here are my questions:
1. Can I unground my single-phase system but ground all the metal cases?
2. what is the pros and cons if I unground this system?
3. if I measure the L1/L2 to the ground, what voltage I would expect?