ctaylo360860
Senior Member
- Location
- colorado
- Occupation
- ME
Existing work has a single phase step down transformer fed from 40amp breaker in a 400amp 3phase 277/480volt main panel. Existing electrician fed primary side of step down transformer with 2 phases, a neutral, and a ground.... everything in the 400amp pane is bonded. the secondary side transformer feeds a 100a panel where all neutrals and grounds are bonded... as I understand this is not correctly done, but I’d love to hear any input on why the existing electrician did this... Transformer should only be fed with 2 phases and a ground on the primary side. There should be a supply side bonding jumper installed inside the transformer sized on 250.102(c) that binds the neutral and the frame of transformer. There should also be an electrical grounding conductor set for the transformer and main panel. Secondary side should feed over to 100amp panel with four wires. 2 phases , neutral, and a ground. Where all neutrals and grounds should be isolated.