I have a 480v,1 phase service,with a roto-phase making the 3rd leg for a 50hp pump and well house. Money issue. Its believed the POCO had a spike and it blew out the VFD in the pump control panel. Solution was to install a outdoor isolation xfmr to help protect the drive and to regulate the 490/508v incoming power.
Here's the deal,out of a transfer switch I tapped one set of 1ph w/grn 480vfeeders to the building no neutral,which feeds a OCPD. The other tap is a 3phase 480v set w/grn to the isolation xfmr,which feeds a VFD control panel.The OCPD panel bonds the building water and structure.
I grounded the xfmr case with the EG and the 1-line shows the XO going to the VFD control panel ground bar.There's no neutral.
Now I believe I have to bond the XO to the xfmr case,but do I have to run a bond to the 1st service OCPD? or am I wrong all together.
Thanks for any guidance.