A small single phase, 480V-120V, 2W secondary, dry type transformer is fed from a CB in a 480V MCC lineup in an industrial plant. The transformer, in turn, feeds a CB panel with main. Isn't it proper to bond the neutral to ground at the transformer only,and have the neutral bar in the CB panel isolated from the panel? The CB panel ECG would then be the RMC that is connected between the transformer case and CB panel.
Is such a dry type transformer in an industrial plant treated as a "separately derived system" per the NEC Art. 100 of such a system?
Is such a dry type transformer in an industrial plant treated as a "separately derived system" per the NEC Art. 100 of such a system?