brian john said:Most clamp on test I see have problems due to the location of the test and/or downstream grounds on the neutral/grounded conductor.
The 4-point test is generally utilized prior to designing a grounding system to determine the resistivity of the soil and the size of the ground system to achieve a specification.
The 3-point test is taken on the made electrode disconnected from the service (which is why the clamp on was designed). Typically you need to go a minimum of ten times the made electrode out to the farthest test probe . Then drive the second test probe at 10% increments and at 66% position. This is completed is several directions (3 or 4 complete test). The Curve that is derived from these test is reviewed and if the curve does not show you are outside the sphere of influence you redo the test at a greater distance.
In my expierence most folks do not want to go to this extent and drive one probe at 100" and second probe at 66' take a measurement and walk away.
for starters
http://www.aemc.com/techinfo/techworkbooks/ground_resistance_testers/950-WKBK-GROUND-WEB.pdf
Exactly what are you trying to check. The previous answers are about testing the ground resistance of the grounding electrode. Is that what you are doing?cakre said:Do I need to switch OFF the power from the panel where I am taking the resisstance meassurement and if i need to check the bonding between the ground and neutral in main panel.Could pleas give me the specific artical in NEC Code book where i can read about that.
Thanks
cakre said:I am trying to take ground resistance on the each panel. I talk to my supervisor and i explain that i do not need to switch OFF the main breaker to take the readings with the clamp meter or with the 3 points metod but he insist on that that the main breaker need to be OFF and then i could proceed with the meassurement.but we have a problem. by the main panel.the generator over there if we shuted off we can not restarted by "X" reasons.
So mine MAIN QUESTION is: DO I NEED TO SHUT OFF THE MAIN BREAKER OR GENERATOR TO TAKE ACCURATE REDINGS WITH THE CLAMP METER OR 3 POINT METOD OR NOT.
Thanks for any answers and any concerns from your side gents.
Exactly what are you trying to check. The previous answers are about testing the ground resistance of the grounding electrode. Is that what you are doing?
Yes (highly likely)cakre said:So mine MAIN QUESTION is: DO I NEED TO SHUT OFF THE MAIN BREAKER OR GENERATOR TO TAKE ACCURATE REDINGS WITH THE CLAMP METER OR 3 POINT METOD OR NOT. ...
Problem is the AEMC Clamp-On , and 3-Point Fall-Of-Potemtial Test cannot be done on the EGC in branch panels. Well the AEMC can be used in the Main Panel if clamped to the right cable like the MBJ or service grounded circuit conductor.cakre said:I am trying to take ground resistance on the each panel. I talk to my supervisor and i explain that i do not need to switch OFF the main breaker to take the readings with the clamp meter or with the 3 points metod but he insist on that that the main breaker need to be OFF and then i could proceed with the meassurement.but we have a problem. by the main panel.the generator over there if we shuted off we can not restarted by "X" reasons.
So mine MAIN QUESTION is: DO I NEED TO SHUT OFF THE MAIN BREAKER OR GENERATOR TO TAKE ACCURATE REDINGS WITH THE CLAMP METER OR 3 POINT METOD OR NOT.
Thanks for any answers and any concerns from your side gents.
The problem, as noted by others, is that you would use a clamp-on ground resistance tester or a 3 points fall-of-potential ground test to measure the resistance of a ground rod. This is something you would do at the ground rod not at each panel. You could use a clamp-on type tester anywhere that the grounding electrode conductor is accessible, which might be at a panel. Thus all of the questions asking what you are actually testing.cakre said:I am trying to take ground resistance on the each panel. I talk to my supervisor and i explain that i do not need to switch OFF the main breaker to take the readings with the clamp meter or with the 3 points metod but he insist on that that the main breaker need to be OFF and then i could proceed with the meassurement.but we have a problem. by the main panel.the generator over there if we shuted off we can not restarted by "X" reasons.
So mine MAIN QUESTION is: DO I NEED TO SHUT OFF THE MAIN BREAKER OR GENERATOR TO TAKE ACCURATE REDINGS WITH THE CLAMP METER OR 3 POINT METOD OR NOT.
Thanks for any answers and any concerns from your side gents.