In a grounding class sponsored by the NFPA, the instructor insisted that the building steel frame could not be used as a ground for a separately derived system unless it was
A. Bonded to the main service entrance ground bus (obviously)
and
B. "Intentionally grounded" at several points i.e. there was a separate ground connection from the building steel to a ground rod, to a ufer ground, or a ground ring in addition to being bonded to the main ground bus.
I can't find any support in the code for B.
Assuming the main service entrance ground bus is properly connected to the water pipe, a ground ring, and a ufer ground, are these ADDITIONAL connections between the building steel frame and one of the grounding methods required?
What are the advantages or disadvantages of adding, say, a ground rod at each corner of a steel frame building bonded to the steel? Or bringing out a bare copper cable from some rebar and bonding it to the steel frame at 4 corners of the building? Do the steel bolts that hold the frame to the concrete bond it to the the rebar system, or are they not connected to rebar? Would these extra ground connections provide some protection against lightning, providing a ground path for lightning that hits the steel frame?
A. Bonded to the main service entrance ground bus (obviously)
and
B. "Intentionally grounded" at several points i.e. there was a separate ground connection from the building steel to a ground rod, to a ufer ground, or a ground ring in addition to being bonded to the main ground bus.
I can't find any support in the code for B.
Assuming the main service entrance ground bus is properly connected to the water pipe, a ground ring, and a ufer ground, are these ADDITIONAL connections between the building steel frame and one of the grounding methods required?
What are the advantages or disadvantages of adding, say, a ground rod at each corner of a steel frame building bonded to the steel? Or bringing out a bare copper cable from some rebar and bonding it to the steel frame at 4 corners of the building? Do the steel bolts that hold the frame to the concrete bond it to the the rebar system, or are they not connected to rebar? Would these extra ground connections provide some protection against lightning, providing a ground path for lightning that hits the steel frame?