B boatfull Member Oct 2, 2007 #1 if a transformer is attached to a receptacle and just the 24volts are brought into a metal alarm cabinet, does it require grounding? thanks
if a transformer is attached to a receptacle and just the 24volts are brought into a metal alarm cabinet, does it require grounding? thanks
barbeer Senior Member Location Pinellas County, FL Oct 2, 2007 #2 Not IMHO, if a phone line is attached a surge arrester should be used on it which would be more effective with a ground point.
Not IMHO, if a phone line is attached a surge arrester should be used on it which would be more effective with a ground point.
Pierre C Belarge Senior Member Location Westchester County, New York Oct 2, 2007 #3 Take a look at 250.20 and 250.22 for grounding of the circuit you are speaking of.
brantmacga Señor Member Location Georgia Occupation Former Child Oct 2, 2007 #4 i think all the alarm cabinets i've installed specified a separate EGC connected to the cabinet.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Oct 2, 2007 #5 The alarm circuit does not require grounding (see 250.20 and exceptions), but the mfg may want the cabinet "grounded" for lightning protection.
The alarm circuit does not require grounding (see 250.20 and exceptions), but the mfg may want the cabinet "grounded" for lightning protection.
brantmacga Señor Member Location Georgia Occupation Former Child Oct 2, 2007 #6 but the mfg may want the cabinet "grounded" for lightning protection. Click to expand... yes, that is what i meant by "specified".
but the mfg may want the cabinet "grounded" for lightning protection. Click to expand... yes, that is what i meant by "specified".