If I have a piece of EMT that is run in a block wall and stubbed out near the structural steel overhead.
I then run a THHN copper conductor (equipment grounding conductor) from a transformer at the floor into the conduit and then out the top of the conduit then cadweld the conductor to the building steel.
Per the 1999 NEC 250-64(e) do I need a grounding bushing on each end of the conduit?, or just one end?, or not at all?
If a grounding bushing is required is this because of the potential for the length of conduit to become energized even though it is an insulated conductor?
Thanks,
Ed
[ October 28, 2003, 05:28 PM: Message edited by: ed downey ]
I then run a THHN copper conductor (equipment grounding conductor) from a transformer at the floor into the conduit and then out the top of the conduit then cadweld the conductor to the building steel.
Per the 1999 NEC 250-64(e) do I need a grounding bushing on each end of the conduit?, or just one end?, or not at all?
If a grounding bushing is required is this because of the potential for the length of conduit to become energized even though it is an insulated conductor?
Thanks,
Ed