480 volt 3phase from switch gear breaker to main disconnect on outside of building, from disconnect to MCC ran with pvc jacketed mc cable. Is a bonding bushing required from disconnect to MCC and/or the main disconnect on building.
Check 250.97. If concentric or eccentric knockouts are not encountered, 480v circuits on the load side of overcurrrent devices do not normally required bond bushings.