Alwayslearningelec
Senior Member
- Location
- NJ
- Occupation
- Estimator
When using a MIGB are they usually only installed at pull boxes or everywhere along the run where the conduit terminates? Equipement etc.? Thanks
No specific situation right now. Just a general thought and question. So if the engineer specifies them but the application you explain does not apply they are not required?What is the application that requires them? Unless you're using boxes or enclosures where there are concentric or eccentric KOs and over 250 volts to ground they're not required. For decades I laughed at guys who insisted that they're required for transformers.
They are rarely ever required. If the voltage is 208Y/120 or 120/240 they are not required even for concentric and eccentric KO's. For 480Y/277 they're required when there are concentric or eccentric KO's in certain equipment like disconnect switches. For 4" or 5" boxes at that voltage they're not required. If your job has all full punched KOs they are not required.No specific situation right now. Just a general thought and question. So if the engineer specifies them but the application you explain does not apply they are not required?
Are they? What about a bonding locknut?They are required on services
They are required on services
Are they? What about a bonding locknut?
Would it be accurate to say that the conduit itself may be bonded at only one end, but a means to do so must be provided for at both ends, because it's a box requirement, not a conduit requirement?The flaw in that flowchart is a metallic raceway needs a bond in every non-metallic box it hits for the non-metalic box to be permitted by 314.3 Ex 1.