I have read in 300.4(F), that you must use an insulated fitting when the conductors are #4 AWG or larger. My question is, when do you need to use a grounding bushing? Where is it in the code book?
 
The most common need for a bonding bushing is on the line side of a service. Take a look at 250.92(B) for methods of bonding at a service.

Chris
 
raider1 said:
The most common need for a bonding bushing is on the line side of a service. Take a look at 250.92(B) for methods of bonding at a service.

Chris


That's true, but even then a bonding bushing isn't required. You could use a bonding wedge or a bonding locknut to satisfy the requirement, provided the KO is the same size as the raceway.
 
infinity said:
That's true, but even then a bonding bushing isn't required. You could use a bonding wedge or a bonding locknut to satisfy the requirement, provided the KO is the same size as the raceway.

Agreed, In my area a bonding bushing is easier to get then a bonding wedge or bonding locknut. When you ask for a bonding locknut, or bonding wedge at the local supply house they usually just give you a funny look and give you a bonding bushing.:D

Chris
 
Two other areas need consideration. First, 250.97, bonding for over 250 volts. Second, 250.100, bonding in hazardous locations. Also check out 501.30, 502.30, and 503.30 for the locations called out to be bonded in 250.100, from the classified area all the way to the point of grounding for service equipment or separately derived system.

Fred
 
Also, underground PVC feeders that change over to RMC to penatrate the

slab,or the earth for that matter, need to bond that metal peice.
 