Aren't they at least "other metal piping"?
I have applied bonding jumpers from water pipe to drain pipes before in cases where there was a elevated grounded conductor voltage - likely just voltage drop but could have even come from POCO MGN. Water pipes were bonded to electrical system and operating at this same potential but because drain pipe in bathtub was not bonded it was at ground potential since it eventually ran into the ground, so users would experience a small voltage between supply piping and drain - the drain was continuous with water as well as the cast iron tub, so just being in the tub and touching the faucet gave you a tingle.
Bonding jumper between water supply and drain pipes eliminated the potential difference.