When grounding the nearest cold water and gas, can you do it in one run? Or do you need to hit the cold water and gas on a separate run?
When grounding the nearest cold water and gas, can you do it in one run? Or do you need to hit the cold water and gas on a separate run?
When grounding the nearest cold water and gas, can you do it in one run? Or do you need to hit the cold water and gas on a separate run?
Locally, I am required to run #6 to bond gas piping.
Locally, I am required to run #6 to bond gas piping.
Locally, I am required to run #6 to bond gas piping.
What type of gas pipe, CSST? Normal black pipe requires nothing more than what has been mentioned above.
Agreed Csst is a different animal however the standard black iron pipe for gas may be bonded using the equipment grounding conductor. Look at 250.104(B)
Says who and is it actually required or a inspector who doesn't know his stuff? I have inspectors require that all the time even though it is not in any codified local amendment
Black Iron
Third party inspection agencies in these parts. Every inspection agency requires the same thing......bonding of gas line whether its CSST or Iron. I don't remember if the requirement is coming from POCO or through a NYS chapter of IAEI, but I can assure you every inspection agency providing services in the area is on the same page and requiring the #6 bond.