Dennis,
I wasn’t sure if you were directing your post at mine above or not… (…If your were… Sorry I can be really slow, sometimes)
My research into the two above noted NFPA documents did not reveal any language which prohibited the bonding of these interior metal water piping systems (as required in the NEC Section 250.104).
I understand, as you do, that many times a dielectric fitting is installed which isolates the interior piping from the exterior piping. I only found this addressed here:
NFPA 13-2007: Standard for the Installation of Sprinkler Systems
Underground piping: Section 10
10.6.7 When it is necessary to join metal pipe with pipe of dissimilar metal, the joint shall be insulated against the passage of an electric current using an approved method.
(...I certainly could have missed something, I am not as familiar with these documents...)
With or without the dielectric fitting, the underground fire protection piping is still not permitted to be utilized as part of the grounding electrode system.
And Yes, I would agree, if an electric fire pump is present, the EGC on the pump will provide bonding for the metallic piping system (Note: a remote pump building may incorporate dielectric fittings separating this pump building’s metal piping from the occupancy building’s metal sprinkler piping system) ...I have seen some fire protection systems which had no pump...
In either case of dielectric ftg. incorporated or no dielectric ftg., if this is actually sprinkler piping in question, this is a bonding issue and not a grounding electrode issue, and for bonding; where that bonding connection is made to the interior piping system is not designated… (...not required at point of origin...)
Am I understanding this correctly ??
mweaver