I have some questions about Mikes grounding concept.
Maybe I should tell you my concept of grounding and you can pick it apart.
1. The 1897 Electrical Code grounding requirements were to control static electric, and for lightning protection.
2. Utility ground to increase reliability of their distribution systems.
3. Utility prefer multiple grounding point, because of their increase grounding points it will insurance against the entire loss of the return path back to the source.
4. The purpose of utility grounding is to provide practical methods of grounding for the safeguarding of employees and the public from injury that may be caused by electrical potential on electric supply or communications facilities, by being able to ensure that the return path is not broken, so as to operate the overcurrent protection devise.
5. NEC grounding is to help prevent accidents to persons and damage by fire to property in case of lightning, breakdown between primary and secondary windings of the transformers, or accidental contact between high-voltage wire and low-voltage wires. If some point on low-voltage circuit if grounded:
1.Lightning striking the wires will be conducted into the ground
2.Breakdown of the transformer insulation between primary and secondary coils will reveal itself through blowing of the primary transformer fuses if one wire of the primary circuit comes in contact with one of the secondary wires.
6. Keeping in mind that the utility does ground their system and the ground (earth) is used as parallel path back to its sources. If the secondary side of the transformer is not grounded, and a crossover does occur the primary 7621 volts, (on a four wire 13.2KV destitution system) would be impressed on the secondary system. The insulation of the secondary system only 600 volts, numerous insulation breakdowns would occur, which would cause considerable damage to equipment installed on a grounded surface (earth), and there would be an extreme damager to human life when coming in contact with any part the secondary system.
7. I do agree that lightning does not protect electrical or electronic equipment from lightning voltage transients induced onto the circuit conductors.
8. I do feel that bonding of source and all noncurrent carrying metal parts is to ensure a low impedance path back to the source to operate the overcurrent protection device.
I hope I have been able to explain my concept, so that you tell me where I want wrong.
Maybe I should tell you my concept of grounding and you can pick it apart.
1. The 1897 Electrical Code grounding requirements were to control static electric, and for lightning protection.
2. Utility ground to increase reliability of their distribution systems.
3. Utility prefer multiple grounding point, because of their increase grounding points it will insurance against the entire loss of the return path back to the source.
4. The purpose of utility grounding is to provide practical methods of grounding for the safeguarding of employees and the public from injury that may be caused by electrical potential on electric supply or communications facilities, by being able to ensure that the return path is not broken, so as to operate the overcurrent protection devise.
5. NEC grounding is to help prevent accidents to persons and damage by fire to property in case of lightning, breakdown between primary and secondary windings of the transformers, or accidental contact between high-voltage wire and low-voltage wires. If some point on low-voltage circuit if grounded:
1.Lightning striking the wires will be conducted into the ground
2.Breakdown of the transformer insulation between primary and secondary coils will reveal itself through blowing of the primary transformer fuses if one wire of the primary circuit comes in contact with one of the secondary wires.
6. Keeping in mind that the utility does ground their system and the ground (earth) is used as parallel path back to its sources. If the secondary side of the transformer is not grounded, and a crossover does occur the primary 7621 volts, (on a four wire 13.2KV destitution system) would be impressed on the secondary system. The insulation of the secondary system only 600 volts, numerous insulation breakdowns would occur, which would cause considerable damage to equipment installed on a grounded surface (earth), and there would be an extreme damager to human life when coming in contact with any part the secondary system.
7. I do agree that lightning does not protect electrical or electronic equipment from lightning voltage transients induced onto the circuit conductors.
8. I do feel that bonding of source and all noncurrent carrying metal parts is to ensure a low impedance path back to the source to operate the overcurrent protection device.
I hope I have been able to explain my concept, so that you tell me where I want wrong.