We recently had a situation where a tap box in a gear lineup was replaced with a 480V, 4000A breaker. The tap box used to serve as a line side tap and feed outside to a solar disconnect where the neutral and grounds were bonded. Since the system now has a main breaker instead of a tap, the conductors that feed to the existing disconnect outside are no longer considered service entrance conductors, they are now a regular feeder. Also this means that the neutral to ground bond must be removed.
The problem is that the grounding conductors run with the parallel sets are now sized too small. They are 3/O and should be sized at 500KCML for the 4000A breaker. The feeders are also in 4" rigid metal conduit. Also because of the size and voltage, the GFP on the new main breaker is limited to 1200A for 1 sec per 230.95
The install is on 2017 code
The problem is that the original plans called for grounds to be routed with the phase conductors. Otherwise there wouldn't be an issue because the conduit could act as the ground. My thought is that since the NEC 230.95 requires the GFP to be set at 1200A and T250.122 states that a 1200A breaker would need a 3/O ground there is a good case for leaving the size as is. This would have to be under engineering supervision...
Unfortunately, I don't see a path to make this code compliant without removing or upsizing the grounding conductors. Please let me know if I may be missing something...
The problem is that the grounding conductors run with the parallel sets are now sized too small. They are 3/O and should be sized at 500KCML for the 4000A breaker. The feeders are also in 4" rigid metal conduit. Also because of the size and voltage, the GFP on the new main breaker is limited to 1200A for 1 sec per 230.95
The install is on 2017 code
The problem is that the original plans called for grounds to be routed with the phase conductors. Otherwise there wouldn't be an issue because the conduit could act as the ground. My thought is that since the NEC 230.95 requires the GFP to be set at 1200A and T250.122 states that a 1200A breaker would need a 3/O ground there is a good case for leaving the size as is. This would have to be under engineering supervision...
Unfortunately, I don't see a path to make this code compliant without removing or upsizing the grounding conductors. Please let me know if I may be missing something...