edit: header should have been "grounding electrode conductor connections"
I was presented a outlook different from my own by another inspector, and, to me, it merits consideration:
Situation: (a) Building with effectively grounded steel framing
(b) Grounding electrode conductor from service disconnect
to steel.
{c} Metallic underground water system
(d) Water piping bonded form building steel to water line.
Question: Are the connections to the steel (b) & (d) required to be ?irreversible? (ref 250.64(c) {2002}).
In his opinin, in this siruartion, then steel becomes a "condcutor" since it
is used to connect the two conductors together (condcutir from srvice and to water) and 250.64(c) applies {2002}.
Not the way I looka t it, but interesting enough that I wanted other opinions.