We installed # 1/0 system grounding conductor without a raceway all the the way to grndg rod & water pipe
through the studs of new home.
is this correct??

tanx
 
hi
We installed # 1/0 system grounding conductor without a raceway all the the way to grndg rod & water pipe
through the studs of new home.
is this correct??

tanx

Maybe not. Where did you run the GEC from/to? No CEE? Most jurisdictions require 2 ground rods (you mention one rod) or first rod to pass resistance test (<25ohms). Where is the water pipe grounded in relationship to where it enters the structure? What size is the service?

http://s3.photobucket.com/user/jwelectric/media/groundingelectrode04.jpg

If you are just asking can you run the GEC thru the studs w/o raceway, then disregard all that ^. Yes, you can.
 
The '11 Code actually added wording to confirm that practice in 250.64(B),
 