J jbfarland Member Sep 10, 2010 #1 Ist it permissable to in stall grounding conductor for ag. building 90amp sub panel feeder 240v single-phase in ditch next to pvc conduit w/ the other conductors.
Ist it permissable to in stall grounding conductor for ag. building 90amp sub panel feeder 240v single-phase in ditch next to pvc conduit w/ the other conductors.
raider1 Senior Member Staff member Location Logan, Utah Sep 10, 2010 #2 Welcome to the forum. Installing an equipment grounding conductor outside of a conduit in a trench would be a violation of 300.3(B). Chris
Welcome to the forum. Installing an equipment grounding conductor outside of a conduit in a trench would be a violation of 300.3(B). Chris