Grounding conductor routed separate from circuit conductors
greenspark1
New England
The situation- an existing service panel (call is Z) with a wireway above. The previous electrician installed a 4/0 ground up into the wireway terminating into an insulated busbar. This then runs to the building's water main.
We're adding a new panel (call it Y) 10' away. The new panel will be fed from Z. The electrician want to tap the busbar in the wireway and run a small conduit down to Y for the ground, and run a new conduit from Y to Z with the 4 phase conductors. This is 208/120V. Is this legal to have the ground in a separate conduit than the phase conductors? It feels wrong but I'm having trouble pinpointing anything in the Code, 250.134(B) seems like the right spot. Anyone run into this before???
When you say "ground" do you mean the EGC, a GEC or just the current carrying grounded conductor of a wye system?
Normally neither an EGC nor a GEC will connect to an insulated bar.
Tapatalk!
It's a hybrid :) The wire is run from the ground bus of service panel Z up to the hunk of copper bus, should have called it a ground bar.
A separate wire (GEC) runs from the ground bar to the water main. This is a GEC, except that it doesn't terminate in panel Z.
It seems like they are trying to combine a GEC and EGC onto one ground bar. I am thinking I should leave it alone and run a standard EGC with the phase conductors to the new panel.
The EGC must be run with the feeder conductors. It could be a metallic raceway instead of an EGC within the raceway. Once you have the EGC with the feeder you can run another conduit to the ground bar with a single conductor if you so desire.