Which table 250.66 or 250.122 is used for feeder from main panel or disconnect at service entrance to a panel(with breakers) located some where in the building--example: 600 amp service entrance panel(six breakers) with 200 amp breaker(1 phase)with 3/0 cu thhn/thwn conductors to 200 amp panel? Use Table 250.122 is definately used for grounding conductor size from the final (200 amp) panel to the equipment(range or etc.). Table 250.66 is definately used for grounding conductor size for the main panel or disconnect at the service entrance. Thanks