Re: grounding conductor size
Ok so tell us how do you ground the 1800 amp service, and what is the size of the GEC, is what the poster wants to know, all we have thrown out is opinions and thougts but no answer, much like my answer it has been shot down, Joe Tedesco where are you!
The way I understand this is, the main grounding electrode is the cold water pipe, ground rods, ground loops, building steel, etc. are all supplemental electrodes, per the 1999 Nec handbook:
If a gec is run from the service equipt. or separatly derived system to a water pipe or structural steel, the gec must be full size per T. 250-66. If the gec from the service equipt. were run , for example , to the ground rod first and then to the water pipe, the conductor to the ground rod would also have to be full size.
In the area where I work (DFW, Texas) it is common practice to run 1 gec to cold water pipe then 1 gec to the ground rod, both full size, if bldg. steel is present we bond, with a full size gec, from water pipe to bldg. steel we also bond the ground and nuetral bars at the main service. Now what the poster wants to know is what size gec is needed for his 1800 amp service he is not asking the size of the bonding jumper from the main gec to the ground rod, that is why, according to my math the main gec is 3/0.
DON I have edited my post sorry for the misprint at the start of my post.
[ September 19, 2003, 08:15 PM: Message edited by: jro ]