If you have to increase the conductor size to compensate for voltage drop, does the EGC have to be increased? If so, how do you determine what size EGC that needs to be installed?
Yes 250.122(B). Read thisroger3829 said:If you have to increase the conductor size to compensate for voltage drop, does the EGC have to be increased? If so, how do you determine what size EGC that needs to be installed?
Dennis Alwon said:Yes 250.122(B). Read this
roger3829 said:Seems like over kill
roger said:Yes it does but, that is the requirement.
The article section needs some work.
Roger
I understand but that is what the code requires.roger3829 said:So..... a 20a circuit normally would require #12 with a #12 EGC.
Upsizing to #4 for voltage drop, #4 EGC????
Seems like over kill
Nope, for 15 through 30 amp circuits the EGC will need to be the same size as the ungrounded conductor(s)D-Nice said:How long is the run? You might be able to go with a #8 copper EGC.
D-Nice said:How long is the run? You might be able to go with a #8 copper EGC.